Forum Discussion
wa8yxm
Jun 23, 2014Explorer III
From the Xantrex Prosine 2.0 manual.
Charge Algorithm: Generic Flooded Wet Cell
Comment Temp Coeff. -27 MV/Degree C
Bulk / Absorption Max voltage 13.4
Max current: 30% (of 20 hour amp hour rating) amps
Float* 13.5 volts
Equalize 17.5 volts
You can trim that a bit, Frankly I think 17.5 is a bit hot. And that is only a partial profile, to get the entire profile I'd have to ask the inverter, not it's manual.
Charge Algorithm: Generic Flooded Wet Cell
Comment Temp Coeff. -27 MV/Degree C
Bulk / Absorption Max voltage 13.4
Max current: 30% (of 20 hour amp hour rating) amps
Float* 13.5 volts
Equalize 17.5 volts
You can trim that a bit, Frankly I think 17.5 is a bit hot. And that is only a partial profile, to get the entire profile I'd have to ask the inverter, not it's manual.