Usnthedog wrote:
wa8yxm and 3 tons. Thanks. Please reread my OP. No hot water heater. (on demand propane only) Only with the converter breaker on doe it trip. Checked continuity between ground and hot on the outside entrance plug. No onboard generator. Refer on caused no problem. Only when the converter breaker is on. And please don't get upset with "please reread the post" it wasn't intended like you thought it was.
Thanks
Jeff
Ok, got it…so assuming no inverter or generator (i.e. no floating ground), unplug shore power and with converter breaker switched to ON, check for unwanted continuity between the neutral and ground bars at the main…There should be no continuity (unless you have a floating ground at a genny or inverter) - neutral and ground bars should NOT have continuity….
3 tons