MEXICOWANDERER wrote:
CAN NOT DRY OUT AGM UNLESS THEY CONSTANTLY VENT but you can damage the plates.
Actually it IS very possible to dry out AGM just like a "gelcell" can also be dried out. Just takes a lot of overcharging which leads to popping the vents and all of that moisture which is supposed to be captured and recombined goes right out the vent.
Have seen this with UPS units which were equipped with AGMs from factory, some bad enough that 2-3yrs is the best you will get from them..
AGMs like Gel cells hate being overcharged and actually AGMs are more sensitive to being overcharged than gels.
BOTH AGM and gels are far less forgiving to overcharging than FLA.
See
HERE"As with all gelled and sealed units, AGM batteries are sensitive to overcharging. A charge to 2.40V/cell (and higher) is fine; however, the float charge should be reduced to between 2.25 and 2.30V/cell (summer temperatures may require lower voltages). Automotive charging systems for flooded lead acid often have a fixed float voltage setting of 14.40V (2.40V/cell); a direct replacement with a sealed unit could overcharge the battery on a long drive."And RV multistage converters can easily do that by staying in bulk or equalization mode instead of dropping to storage mode or staying in bulk or equalization mode too long or too often.
OP has boiled their FLAs to death, fair chance that their setup if not checked properly will do the same to the AGMs.
There are "pros" and "cons" to AGM, pick your poison.