- westomExplorer
MEXICOWANDERER wrote:
If a 12.5KV line should drop upon a 3KV line no device I know of is going to protect a service drop. >KV relay switches are used in transmission not distribution networks. Let's avoid lumping all forms of disturbances into a grand mishmash.
Appreciate that some claim experience and knowledge - that contradicts over 100 years of science and experience.
A 33,000 volt wire fell onto local distribution. Plastic glass from electric meters exploded 30 feet from their pans. (I never saw that before or again.) Many had destroyed protectors and damaged appliances that they assumed would be protected. At least one had multiple destroyed circuit breakers.
But my friend knows someone who has done this stuff for decades. His meter also exploded from its pan. But he had no damage even to MOVs in his 'whole house' protector. He installed and properly earthed what an engineer recommends.
All homeowners psid to replace damaged meter pans. Electric company is not responsible. Another should have known that.
Why does one *know* damage from a dropped 12.5Kv line cannot be averted? Wild speculation with deceptive numbers and near zero experience does not constitute knowledge.
Best protection from a typical campground surge is a Progressive or something equivalent. Best protection from a rare campground surge (ie a microsecond transient such as lightning) requires a Progressive type device located (low impedance) as close as possible to a pole and earth ground. Since MOVs protect from that type of surge only when connected low impedance (as short as possible) to earth.
One knows protection from 12.5Kv is imppossible because he did not do this stuff. Different 'surges' require different solutions. For surges typically found in campgrounds, a Progrssive was always highly recommended. To protect RVs from surges created by lightning requires a protector be attached at the pole - as close to earth ground as possible. - westomExplorer
pianotuna wrote:
So is the 20,000 amps from a lightening strike? Or?
A surge also known as a spike, transient, or direct lightning strike can even be a 20,000 amp microsecond event. Homeowners earth a 'whole house' protector so that robust protection already inside appliances (up to 600 volts for 120 volt appliances) is not overwhelmed. So that current is not inside hunting for earth destructively via appliances.
Informed homeowners properly earth a 'whole house' protector.
Campgrounds typically suffer from other surges including low and high voltages that might rise above 140 volts or drop below 90 volts. These typically exist for seconds or hours. RVs need a Progressive type protector especially for motorized appliances that are at greatest risk from this anomaly.
Electronics appliances are perfectly safe for all voltages below 120 volts. Motorized appliances are not.
Progressive that addresses these anomalies is highly regarded.
A Progressive protector is for common anomalies found in campgrounds. MOVs do little for typical campground anomalies. A 20,000 amp transient is a rare anomaly averted by MOVs in a homeowner's 'whole house' protector because it is earthed. So that all appliances are protected for tens of years. Properly sized and properly earthed MOVs do not fail as others would have us believe.
A third device, a plug-in protector is ineffective for both requirements. Plug-in protectors address a completely different anomaly typically made irrelevant by protection already inside all appliances: electronic and motorized. MOVs in plug-in protectors can be grossly undersized to fail in a sacrificial manner. These are marketed to naive consumers with obscene profit margins. Undersizing and a resulting catastrophic failure gets naive consumers to assume sacrificial MOVs are acceptable.
Protectors for RVs are for anomalies completely different from properly earthed protectors for homes, businesses, factories, broadcast stations, munitions dumps, server centers, and telephone COs. Different anomalies (all called surges) require different solutions (all called protectors). - westendExplorer
pianotuna wrote:
Hi Mex,
Yes, please. But with a wiring diagram for dummies in a parallel (not series) configuration (that would make it plug and play).MEXICOWANDERER wrote:
If there is enough interest in this, I'll shop on eBay and post the seller links for the correct rated devices. REMEMBER minimum 4 devices except GDTs EACH buss. Four, L-N and four L-Ground 20 mm MOVs preferably 1500 watt TVSs. Six each would be better yet. Yes, fuses are vital for TVS circuit protection.
I've got both hands raised, yes, please. - MEXICOWANDERERExplorerNumber One. What I describe uses fuses. Number two if you actually DISASSEMBLE a common "surge protector" you will see it consists of two l-o-n-g brass strip assemblies not the same league as a common 15 amp duplex receptacle. Want my fifty dollar pile of garbage famous brand surge strip?
Number three if you believe a metal oxide varistor is a years-long protector against voltage transients you need to go back to university and smack your professor upside the head. MOVS do indeed fail.
Number four. Work with an oscilloscope when discussing transients. Ever see an event with predominant INVERSE voltage wave form? A MOV S-T-A-R-T-S to react in nanoseconds when a TVS is fully involved.
The idea is to DRAIN not BLOCK positive and negative oriented events. Events deteriorate the integrity of any device but especially power and memory components.
If you need encouragement to believe event suppression is important in recreational vehicles survey the lifespan of appliances. They fail far too often. It is not that they are built differently but subjected to an environment when monitored on a scope will make a person's hair stand on end.
A voltage transient is N-O-T a "surge". Surges that last >100ms need voltage CORRECTION. Someone mentioned a high voltage distribution event. This can overpower even a voltage correction or even an EMS device. Such an event is the responsibity/LIABILITY of the power company.If a 12.5KV line should drop upon a 3KV line no device I know of is going to protect a service drop. >KV relay switches are used in transmission not distribution networks. Let's avoid lumping all forms of disturbances into a grand mishmash.
NEMA and UL regulations were revised because idiots marketed devices that did not incorporate fusing protection. There were indeed fires.
If you wish to argue whether TVS devices are valid do it in front of an oscilloscope. Then have campfire discussions with fellow RVers and tell them common electronics failures are all in their imagination.
If TVS devices were not needed thousands of pages of cataloging and white papers would not exist. IT IS EXPENSIVE for OEM to rice grain fuse protect each and every device. Properly constructed and oriented a GDT / MOV / TVS circuit is both safe and effective. Proper sizing of TVS discretes actually enhance the lifespan of MOVs. Each component serves a purpose and if you carefully re read what I wrote there are enough caveats and exclusions to answer questions.
SURGE PROTECTOR is a hated buzzword. Transient Voltage Protection serves a unique but overlooked purpose. A stepped transformer bucker down here can not react fast enough making ferroresonant voltage correction the only choice for inductive service line protection.
Time spent in front of an oscilloscope really does pay dividends. - pianotunaNomad IIIwestom,
So is the 20,000 amps from a lightening strike? Or? - westomExplorer
pianotuna wrote:
Your post caused me to think about what a Mov does. It doesn't stop the surge, it diverts it.
A protector device that is adjacent to the appliance must either 'block' that current or 'absorb' that energy.
If it (instead) diverts current, well, that was also explained.Assume a surge is approaching on a hot (black) wire that is 5000 volts. What does that protector circuit do. Now that surge is 5000 volts on that hot wire, and 4670 volts on the safety ground (green) and neutral (white) wire. Where is this protection?
If a protector is too close to an appliance and too far from earth ground, then where does it divert that current to? Destructively via some adjacent appliance. An IEEE brochure even demonstrated this in a picture with a number. A protector without an earth ground connected a surge 8000 volts destructively through a nearby appliance ... that was not even connected to that protector.
And that is the point. If that current does not connect low impedance to earth before entering, then nothing can avert a destructive hunt. That current, incoming to everything, selects which item to pass through - destructively.
No protector does protection. Best protection is hardwire connected directly to earth - no protector required. Protectors are used when a wire that cannot connect directly to earth. A protector is only doing what that hardwire does better.
A Progressive that can protect from that anomaly must be located at a pole - to make a low impedance (ie as short as possible) connection to earth ground. Does not matter how good its protector parts are. Even the best protector in the world is ineffective is not connected low impedance to single point earth ground.
UL says nothing about protection. UL (National Fire Protection Association) is only about human safety issues. Protector can be completely ineffective. But still gets UL approval because it did not spit sparks or flame. - pianotunaNomad IIIWestom,
Actually the surge device I added to the Sola is not in the RV. Also the particular device is CSA and UL approved. 2400 joules and 40,000 amps. The device is exterior to the Sola.
I can say the previous device lasted for 3 years but when I checked it this spring it had failed, so I've had some (minor) surges.
20,000 amps would be from a lightening strike? Or? - westomExplorer
pianotuna wrote:
If I add a MOV type device in parallel to the shore power cord will it offer some down stream protection to my RV?
Please step back a minute. Ignore everything posted. First grasp these basic facts. Then read everything to separate half truths from actual facts.
First, this will discuss one type of surge that typically damaged appliances in an RV and appliances in a home. This transient is a current source. That means it has near zero voltage if connected low impedance (ie within feet) to earth ground (not a receptacle's safety ground). It can be 20,000 amps. It is typically a microsecond event.
That means anything that foolishly tries to block it causes voltage to increase even destructively. If anything tries to disconnect from a surge, well 300 consecutive surges could pass through before a disconnect even starts. That means every informed reply always says where hundreds of thousands of joules dissipate.
Second, MOVs in a Progressive only address this anomaly (different from other anomalies also called a surge) if that PI connects at the pole. A protector is only as effective as its earth ground. Only earth ground does that protection. MOVs in a PI are only connecting devices to what does protection.
Third, MOVs are more than fast enough. MOVs will respond in nanoseconds. These type of surges are microsecond anomalies. (BTW, nobody sees the surge. Most confuse the construction of a plasma path that may take hundreds of milliseconds with a surge that is done in microseconds.) However, if MOV leads have sharp bends or that connection to earth ground is too long (ie protector located inside an RV), then that response time increases. Again, protection is about impedance (not resistance).
Four, assume those MOVs in a Progress (inside an RV) are rated at 330 volts (let-through voltage for 120 volt service). Assume a surge is approaching on a hot (black) wire that is 5000 volts. What does that protector circuit do. Now that surge is 5000 volts on that hot wire, and 4670 volts on the safety ground (green) and neutral (white) wire. Where is this protection? Again, protector does not define protection. A majority never get this. Quality of earth ground and its connection defines protection.
Five, why would MOVs need replacement? How many joules does it claim to absorb? Hundreds? A thousand? Potentially destructive surges can be hundreds of thousands of joules. What happens when a protector tries to 'absorb' or 'block' that energy? Effective (properly sized) protectors do not fail. If a protector fails, it was undersized for that venue. Must be replaced by one with larger ratings.
Six, of course, how often do destructive surges occur? Maybe once every seven years. A number that can vary significantly even in a same town. A number determined by relevant factors such as geology.
Why do protectors for RVs typically ignore this type of surge? Progressives address other anomalies that are called surges - such as high voltage, low voltage, open ground, floating neutral, or reverse polarity. Type of surge technically defined above is rare in campgrounds. But is often blamed when others have no idea what else to blame.
Reread those others posts. Any useful recommendation (for this anomaly called a surge) will always say where hundreds of thousands of joules are harmlessly absorbed. Since a protector is only as effective as its earth ground - including impedance of that connection.
One final point. Do not install your own MOVs. Fire and other dangers exist. So many protectors were so badly designed that UL repeatedly upgraded UL1449. UL1449 says nothing about protection. It is completely about human safety issues (including fire) created by so many plug-in protectors.
How many knew even half of this or discussed any of those numbers? - AlmotExplorer III
pianotuna wrote:
Almot,
The Sola bucks down about ten volts. Surge could be 20,000 volts.
The sola is fast at switching modes but true surge protection needs to be at the nanosecond level. I'm certain the Sola is NOT that fast.
Ok, got it.
Stupid question: those ubiquitous $6 "spike-surge-guard-suppressor" - whatever sellers might call it - rated to say, 900 Joule, 15A - how big of a surge or spike could it handle?
(Well, probably not a "spike" since it has no independent ground and thus, according to Mr Wiz, won't handle spike). - MrWizardModeratorTransient Spikes can be thousands of volts and last Milli seconds
Surge can run hundreds of volts and last minutes or longer
The real difference is time , surges last longer than transients
To protect against a spike you short it aka direct it to ground
To protect against a surge , you control the voltage or you disconnect
I think I stated all that correctly
Having RV issues? Connect with others who have been in your shoes.24,303 PostsLatest Activity: Aug 21, 2025