turbopilot51 wrote:
On the display zone one is flashing while zone 4 is not. :h
Because there is a short or communication problem in that phone type cable. Access the roof AC control board. Zone 1, there will be 2 phone type cables connected. Disconnect BOTH. The wall tstat will go dead. Connect 1 cable. If the tstat powers up do a reset and see if Zone 1 AC functions on all modes. If the tstat does NOT power up, that is the cable to the Zone 2 AC. Disconnect that cable and connect the other cable and the tstat will power up. Do the reset and see if all modes function. IF they do, connect the extra cable back to the Zone 1 board. Then do a reset, IF you get the error again then the problem is between the 2 AC units. Disconnect the Phone type cable at the Zone 2 control board and do the reset on the tstat. IF the Zone 1 operates in all modes, then the problem is in that cable between the 2 AC units. The normal procedure is to cut off the modular ends and install 2 new ends and proceed. Doug