rockcandymountain wrote:
While trying to figure out what is wrong with my furnace not wanting to come on. I noticed a red light in the DSI panel that says DSI fault. Would that make it so that the furnace or hot water would not come on? If there is a fault how can it be corrected?
That is one of the easier questions to answer (What triggers the light)
The furnace has a flame sensor (A thermocouple) it may also be igniter spark rod. IF the furnace lights and works normally this rod gets quite hot and starts sending current.. or generating about 0.48 volts (And the current that results from that voltage sent to the control board)
IF the control board does not sense that voltage and current then FAULT (it tries 3 times then goes to fault)
NOW what could cause that to happen. that's a much harder question.. For this you need to step out and remove the outside panel. turn the circuit breaker/switch atop the blower housing OFF and have then set the T-Stat high enough to call for heat.
Outside turn switch on.. You should hear the blower start up and then you may hear the gas valve click, there will be a change in the WOOSH sound as gas flows. And you should hear the snap shap of the ignighter followed by FLAME ON.. If this does not happen.. Post what does and we will continue.
If it does happen. then it will flame off, on off on off and the fault light comes on
Step one is clean the sensor rod. also make sure the burner is coming on strong. If this does work pull the control board to an RV dealer who can test it. I recommend replacement with Dinosaur Board boards.
Way better built.