Extreme Cold+Propane Tanks: Advice Needed!

I know there are several forum members who routinely camp in sub-zero temperatures, and I'm hoping they can chime in with their experiences. I'm hoping next winter to camp WITHOUT hookups in places where temps regularly dip into the single digits (F) or below zero overnight. Temps would rise in the daytime but are not likely to rise above freezing. And as I said I would be boondocking without hookups.

My question for those who camp in cold temps, what can be done to prevent your LP tanks from getting so cold that the gas no longer flows? I see there are tank heaters out there, do they work? And what about the piping? If the LP needs to flow twenty feet outside the cabin before it gets to the LP generator, is that an additional vulnerability? And what should be done? Pipe heaters and/or insulation?

Thanks!
  • Horizontal tanks are far better than vertical cylinders in cold weather, due to the larger "wetted" surface. For vertical cylinders, keeping them as full as possible is the key- they need to absorb the heat for vaporization from the outside-

  • SDcampowneroperator wrote:

    ' Bobs' trouble was due to small tanks that could not boil off enough vapor. fast enough.
    Aint that right. Bob? , 'Tuna?
    Your friend , been there, Max


    Yup! That's right! :)
  • wa8yxm's avatar
    wa8yxm
    Explorer III
    What can be done is to make sure they are full of PROPANE not BUTANE

    Why:
    Vapor temp of PROPANE is roughly -40 (39.something as I recall) at any temp over -30 you will have enough pressure for everything to work.. at -40, it will not.

    NOTE; at -40 it don't matter if you are using "C" or "F". same temp.

    Butane however the vapor point is right around the freezing point of water. So if it's freezing out, it don't work

    SOME stores.. Epically here where I am in the "Sunny South" lie to you and sell the cheaper Butane at Propane prices.. Butane gives slightly more heat per unit volume so nobody comnplains.. But if you get cold. it don't work.
  • Hi Max.

    Yes.

    Insulating the feed line to the generator would be the worst thing you could do unless the ambient was lower than -42.5 C.

    Get a horizontal tank in the 250 to 500 gallon range. They can be rented.

    SDcampowneroperator wrote:

    In temps nearing those lows, only very large tanks, say 250 to 500 gal. tanks can boil off enough vapor to power a 35 k furnace. At minus 40 c or f its all the same,
    ' Bobs' trouble was due to small tanks that could not boil off enough vapor. fast enough.
    Aint that right. Bob? , 'Tuna?
    Your friend , been there, Max
  • I second the propane not butane comment. Filled one of my two tanks in Florida in the early spring and then went north. It froze........ took me a bit to figure the problem out.
  • Professional propane distributors mount infrared heaters to shine on bulk tanks (like 500 gallon size) during bitter cold. DO NOT FORGET THE REGULATOR. Professionals call it "Freeze Up".

    Check with a professional propane distributor (a distributor has a fleet of bulk trucks that fill 500 gallon pad mount tanks). They will give you professional advice.

    In my case 35 years ago I had to change the small RV regulator over to a larger 2 stage regulator to stop freeze up. -29F.