Sounds like it is operating off of the 'high temp' switch---called 'limiting'
Temp comes up to fast a rate of increase..furnace overfiring...high temp switch opens shutting down DC to circuit board. Fan continues to run...high temp switch cools/closes/DC back to circuit board/t-stat still calling for heat so burner fires.....cycle repeats
Causes:
Blocked ducts, too many registers closed/obstructed ----resists air flow
Restricted return air -----minimizes amount of air back to furnace
LP System Pressure.......too much fuel/overfiring
Defective high temp limit switch.....190*F switch #31091
If you remove outside access panel you should be able to see the LED on the circuit board
1-Flash with 3 second pause.......Limit switch/airflow issue
AFM Series Furnace
Temp comes up to fast a rate of increase..furnace overfiring...high temp switch opens shutting down DC to circuit board. Fan continues to run...high temp switch cools/closes/DC back to circuit board/t-stat still calling for heat so burner fires.....cycle repeats
Causes:
Blocked ducts, too many registers closed/obstructed ----resists air flow
Restricted return air -----minimizes amount of air back to furnace
LP System Pressure.......too much fuel/overfiring
Defective high temp limit switch.....190*F switch #31091
If you remove outside access panel you should be able to see the LED on the circuit board
1-Flash with 3 second pause.......Limit switch/airflow issue
AFM Series Furnace