BJean wrote:
I have read the replies and the motor does not have a flat spot but I have encountered this before on other items. It appears that I have a air flow switch problem and will address is Monday.
That is a standard 12 volt Circuit breaker. Either your motor was pulling too many amps or you had a direct intermittent short. A BAD motor can run and still intermittently pull too many amps causing the CB to trip. Air flow has nothing to do with it. Your furnace is 6 years old, the motor may be bad. On your model, the 12 volt power goes to the CB from the furnace On/Off switch. The output side goes direct to the Ignition module and a tstat wire to the wall tstat. IF the wall tstat wire was a short, that will trip the CB but will usually burn out the wall tstat as the CB is a higher amp than the connections on the wall tstat. The odds are you Motor is intermittently pulling too high amps causing the CB to trip. Doug