agiannetti's avatar
agiannetti
Furnace Short-Cycling
2018 Furnace - Atwood/Dometic model AFSD20141 is short-cycling.
I tried the following everything:
Jumped the thermostat
jumped the high temp limit switch
jumped the sail switch
removed discharge vents to assure no blockages
checked return air for obstructions
made sure battery fully charged
(I have NOT yet checked the gas pressure)
I turned the main gas valve to almost closed to lower gas pressure (as evidenced by reduced stove flame) - that corrected the furnace for short-cycling, but only for one day.
MAJOR CLUE TO THE ISSUE: Without fail, when I remove the exterior panel and vent tube, it works fine. The INSTANT I start to replace the panel, the burner shuts off. Is it possible/probable, when I start to put the cover on, the change in airflow disrupts the flame under the electrode and causes the burner to shut off? Would the absence of a strong flame immediately shut off the burner?
  • It cycles every few seconds. I've jumped the high limit switch and the sail switch, but the problem persists.
  • How short is the short cycling? If in seconds it can be the flame sensing not working right. If minutes it can be the limit switch not working right.
    There are a couple of furnace guys on here who might be along to answer your questions.
Having RV issues? Connect with others who have been in your shoes.24,228 PostsLatest Activity: Apr 04, 2025
