Fusing solar

If the controller is 30amp do you fuse the line for 30amps.

15 Replies

  • What brand controller do you have? Post all the facts, not just your question.
  • Morningstar says to comply with NEC the fuse (battery to controller) s/b rated at least 20% over the controller rating and wire should have ampacity to match the fuse. So you are looking at 40 amp fuse and #8 wire minimum afaik. Fuse s/b close to the battery not the controller. If you are pushing near 30 amps I would have #6 wire minimum assuming wire fits the controller lugs.
  • Fuses are to protect the wire between items. Fuse to the wire size. i.e. #10 30 amp, #12 20 amp, etc.

    Rail Dawg wrote:
    If the controller is 30amp do you fuse the line for 30amps.
  • Doesn’t the controler’s manufacturer state the fuse requirements? WindyNation does.