The generator should run at a constant 3600 RPM regardless of the load. It should never run at idle speed. The fan running slower than normal is an indication the generator is running slow. Make sure the throttle linkage is clean and moves freely. Adjust the speed until the voltage is a bit on the high side with no load. Plug in a fairly heavy load such as a hotplate or toaster. The throttle should open up to bring the speed back up to 3600 RPM. Check the voltage to see if it is close to 120 volts.