Generator voltage too high

Recently completed a trip where I had my generator running about 2 hrs while on the road. Class A with Generac Guardian 65. When I arrived at the campsite there was smoke at the transfer switch, and burned wires coming from the transfer switch to the panel. Disconnected everything, and replaced the transfer switch when I got home. Shore power is fine now, but generator is putting out 145 - 148 volts, hz 60. Could this high generator voltage have been the reason the transfer switch burned up? Shore power voltage is 124 and hz is 60. I tried to adjust the voltage regulator, voltage didn't change. I have ordered a new voltage regulator, hope this solves the problem. Any other ideas why high voltage from generator?

6 Replies

  • Thanks for all the quick responses. Swapped out the voltage regulator today. Adjusted hz and voltage and generator purring like a fine Chinese watch. 60-61 hz and 121-2 volts.
  • "...then about only
    thing that would cause high voltage output..."


    A voltage regulator can react under light or medium loads to a high resistance voltage sense lead connection. This means a "negative" connection as well. Might as well cover all the bases :)
  • If speed is correct (you said it is around 60HZ) then about only
    thing that would cause high voltage output is faulty voltage regulator.
    make sure the brushes and slip rings are in good shape. high resistance in field circuit can cause volt. reg to go to full field voltage, then get "stuck" there. This condition can cause new regulator to fail prematurely also
  • I am attempting to dissect 6 different Generac voltage regulators and see what has failed. If it's an 1/8th watt zener I'll replace it with a one watt. They make some pretty impressive bi-polar transistors these days. Same with rectifiers.
  • Could this be your problem, yes
    Higher voltage induces higher current/amps flow thru some of the devices in use,
    This heats up the wiring and the connections

    Or loose connections, can cause heat and resistance, which will alter the generator load and put a strain on the voltage regulator
    It's a two way street
    Hard to say which one came first
    New transfer switch and new voltage regulator should fix everything
  • Regulator bad. Had this happen, burned up old Television, had to replace. Service tech replaced regulator and readjusted. All has been well since.