BB_TX wrote:
Dutch_12078 wrote:
As has been stated, a GFCI trips when it detects an imbalance between the hot and neutral. The ground has nothing to do with it. ......
That part I understand and am not questioning the lack of a ground on the GFCI outlet itself. What I don’t understand is how you can have a ground fault in an ungrounded RV that would trip a GFCI outlet. To have a ground fault that would trip a GFCI outlet there must be some path for the errant current to drain to a ground source. Otherwise there would never be an imbalance in the individual currents thru the hot and neutral pins of the outlet.
I agree. You cannot have a ground fault without a 3rd conductor back to the source. The intent of a GFCI is to prevent the ground wire or a human to earth ground from becoming that conductor. If the only electrical connection between an
insulated RV and the power source are the hot and neutral, a GFCI cannot trip. Current will either flow equally in the 2 conductors or not at all.