road-runner wrote:
When I looked at how they do this, I discovered that the GFCI simply induces current into the wires which in turn trips the very same current imbalance detector. So while no external current is flowing, there is some inside the device. Regardless, an RV without a ground path will not trip from current imbalance or shorted neutral & ground.
The downstream neutral-ground fault detection does not use the current imbalance detector, but rather a different mechanism. An example can bee seen here: http://www.onsemi.com/pub/Collateral/FAN4147-D.pdf
Diagram on page 2, description starts near the bottom left of page 5. Older designs did use 120 Hz. signal injection, but still used a separate transformer for detection.
But the description describes a "grounded neutral" which goes back to the question of how can you have a "grounded neutral" when there is no ground connection at all to the trailer. Current does not flow into an open ended wire. And an ungrounded frame is effectively an open ended conductor.