nebster wrote:
So here's a follow-up question to confirm something I have been presuming for a while:
If the RV is powered via a line+neutral shore cord, with no EGC, and an inline GFI is provided in the shore cord... is a hot chassis event with a human inadvertently providing a low impedance path to earth ground something that the GFI will (should) protect against?
Assuming there are now two faults, one being the floating chassis and the second being the person standing on EARTH being exposed to the 120VAC supply to the RV. Yes, the GFCI would trip.
But if there is only one fault, the open ground (floating chassis), a person receiving the "tingle" while providing the path from the 40VAC CHASSIS to EARTH.
No, I do not think the GFCI would trip.