Gdetrailer
Nov 25, 2020Explorer III
obiwancanoli wrote:
Yes, Gdetrailer, my water heater is both electric and propane, and I have two GFI's - one over the sink, another in the bath... both won't reset, and both seem to be on the same circuit. Can plug in at home, but I'm not there... boondocking northern AZ
Both won't reset pretty much rules out the GFCIs being the issue, highly doubtful that BOTH have had sudden failure at the exact same time.
However, having two GFCIs on the same circuit (one upstream and one downstream) is not recommend. Suspect those will be on two separate circuit breakers.
I suspect since you most likely have a factory inverter installed that there is a ATS (Automatic Transfer Switch) that transfers some circuits to inverter when no shore power is present.
In this setup, sometimes manufacturer will provide a separate small breaker panel for those inverter circuits which may give the appearance that both are on the same circuit from the main panel.
I am not sure you are really going to be able to trouble shoot this while camping, may require a lot of work in the breaker panel to isolate circuits and in the end, it is possible that the inverter may be at fault..
Try unplugging everything from every outlet, if no joy, then try pulling the fridge 120V plug (typically located in the outside access area).
If no joy, you will need to isolate the converter which may be hardwired in the main panel or could be plugged in..
If no joy or no converter, the converter may be built into the inverter which makes troubleshooting a bit difficult..
If no joy continues then you would have to remove and isolate every hot and neutral in the main breaker panel one at a time..
Not really something I would want to do while camping and the reason I mention needing to plug in to shore power to verify all systems are good to begin with..
Can you just plug an extension cord into the inverter for now and limp along?
Having RV issues? Connect with others who have been in your shoes.24,375 PostsLatest Activity: Apr 09, 2026