DrewE wrote:
There's nothing wrong with having a standard 20A GFCI on a 15A circuit (provided the socket itself on the GFCI is a 15A socket, and not a 15/20A combo with a T-shaped slot). The 20A rating is just a maximum. On the other hand, having a 15A GFCI on a 20A circuit is not right.
I have never seen a true 15A only through GFCI (15A face and 15A downstream).
What I have seen is 15A face with 20A downstream GFCIs which is 100% correct and can be used on a circuit protected with a 20A or a 15A breaker.
Outlets with 15A faces are allowed in circuits protected by 20A breaker provided there is more than one duplex outlet.
See
Difference between 15A and 20 GFCI"
Beside this, what is the difference between 15a and 20a GFCI?
By making GFCIs 20A internally but 15A on their face, it allows you to use the same GFCI on both 15A and 20A circuits. If the receptacle had the T-neutral, that would mean it could not be used on 15A circuits. NEC 210.24 allows you to put a 15A receptacle on a 20A circuit if it has 2 or more outlets on a circuit.
Also, what is the difference between 15a and 20a? 15a and 20a receptacles have different pin configurations. A 20a receptacle will have one slot that is turned sideways or T shaped to allow a 20amp plug to be used. A 15amp receptacle on a 20 amp circuit will not overload the circuit. You will only be allowed to plug in 15a devices.
People also ask, can you use a 15a GFCI outlet on a 20a circuit?
A 15 amp GFCI receptacle may be supplied power from a 20 amp circuit. Other that gratuitously degrading the performance of the circuit if only one 15 amp receptacle is used in the circuit, there is no reason why it cannot be done. In fact, most receptacles come in pairs with a potential of up to 30 amps."