No neutral-ground bond anywhere in the RV and not in the new subpanel either.
Only bond should be at the power source such as the main utility panel(not your RV panel). If the inverter internally bonds the neutral-ground as part of normal operation that is OK.
All grounds need to be connected and to the RV frame also. This includes the inverter chassis and the metal subpanel case if applicable.
Only bond should be at the power source such as the main utility panel(not your RV panel). If the inverter internally bonds the neutral-ground as part of normal operation that is OK.
All grounds need to be connected and to the RV frame also. This includes the inverter chassis and the metal subpanel case if applicable.