Forum Discussion

mdock2's avatar
mdock2
Explorer
Aug 29, 2018

HELP!!!!!! with last step of inverter install

I'm finishing up on installing the AIMS Power PWRIX120012S 1200 Watt Pure Sine Inverter, with Built In Transfer Switch. i have installed a sub panel, and should the sub panel be Bonded or not.

Thanks for your help...
marty
  • What exactly do you mean by "bonded" ? In Rvs the main dist panel for the 120v breakers is not bonded. The shore power source panel the pedestal receptacles are on is the bonded one.

    So your sub-panel from the inverter needs to be carefully defined as to what you are doing.
  • "boned"???

    Or did you mean "bonded"??

    If you mean bonded, then the answer is no!! NEC specifies a "sub panel" is to have isolated neutral bus bar, carried back to the main panel.