dougrainer wrote:
Your model specs are based on 115 volts/95 degree ambient
6.7 amps compressor
2.3 amps LO Fan= 9.0 LO fan
2.9 HI Fan = 9.6 HI fan
I am not familiar with a Kill a watt meter system. WHERE and WHAT dies this actually measure? JUST the AC power line circuit? OR, the complete AC amp draw of the RV? If the complete amp draw of the RV, you CANNOT isolate just the AC amps easily. 125 volts????? Where are you getting 125 volts? The Electricity in my area rarely exceeds 121 volts. On GENSET you can get higher voltages. At 125 volts times the 9.6 will yield 1200 watts. 120 volts times the 9.6 will yield 1152 watts. So, your problem may be the higher voltage you have. The RVP SPEC running watts at 115 volts at 95 degrees is 1048 watts. The ONLY sure way of determining the amps is with a digital amp meter AT the AC 120 supply wire. Doug
Thanks to All !!....So at 90df in my garage I took the cover off the rooftop Coleman and using a clamp-on meter at the compressor (excluding fan), I came up with this having no other appliances on...
On shore power:
Shore power volts, no load 117v
Shore power volts w/compressor running 113v
Volts at compressor 111 to 112v
Amps at comp motor (minus fan) 9.2a
On Honda 2200i:
Volts at Generator, no load 127v
Volts at Generator, w/compressor running 124v
Volts at compressor 120v
Amps at compressor (minus fan) 9.4 to 9.5a
The results seem a bit ambiguous, but it appears that the compressor amps are high - If I can believe Colemans specs of 9.0 total amps (incl. fan) at 95df (90df during my test), and the fan is supposedly using about 2.5a, then the actual compressor only amps should be about 6.5a, which (if correct) means that the compressor is using 2.5-3.0 extra amps than the specs call for. Seems like quite an overage to me, yet the air runs fine otherwise - maybe a bad omen awaits - lol
3 tons