High Efficiency 13.5k BTU a/c = Smaller Generator?

Here' some specs (BTU/Compressor Amps/Fan Amps/Inrush-LRA):

Dometic (standard unit) 13,500/12.4/2.5/63
Total amps: 14.9

Colman Mach (standard unit) 13,500/11.9/3.4/63
Total amps: 15.3

Dometic High Efficiency 13,500/8.6/2.5/50
Total amps: 11.1

Coleman Mach 3 PS 13,500/8.3/2.9/58.4
Total amps: 11.2

Once started these high efficiency units use about 3-4 amps less current than the standard units. The Dometic has a respectable 13 amp (63 to 50) reduction in inrush/LRA/startup current. A very good thing for smaller generators.

Did notice the Coleman Mach 3 PS had much less reduction in inrush/LRA/startup current vs. their standard unit. Wonder why? Quite a few small generators will never have the opportunity to see the reduced steady current demands because they'll never get the past the higher inrush/LRA/startup current.

Typically these high efficiency units can be purchased for $650-$750. Purchasing one of these might be a better investment vs. buying a larger generator--say, one EU2000 vs. two EU2000i's--$1000 vs. $2100 :)

25 Replies

  • Dometic does not offer a Hard Start Cap on regular units. I am not aware of Dometic offering a Hard Start Cap as a optional part.
    RVP DOES allow you to option a Hard Start Cap. BUT, that may be OEM only and you have to purchase the Hard Start Cap kit from RVP. When you talk to whoever you are buying from, ask for the Hard Start CAP system. That will usually be a Special order, so it is quicker to just buy the RVP model you want and buy the RVP Hard Start Cap as an extra part.
    If you read the archives, you will find a lot of RV'ers using a non RV Genset having good luck with adding a Hard Start kit. You do NOT have to use the RVP Hard Start kit. You can get one locally from your regular HVAC supply company. Doug
  • wa8yxm's avatar
    wa8yxm
    Explorer III
    Carrier Air V (no longer made) 13.500 BTU 13.5 amps

    Advent Air (Replaces top (Roof) unit on the Carrier when the Carrier fails due to poor construction) 15000 BTU, 13.5 amps.

    (My Front and Bedroom air conditioners,,respectively)
    (Construction fault corrected on front unit...By me).
  • BillyW wrote:
    Do they use a hard start cap? That significantly reduced the initial amperage load on my Coleman MachIII.
    That's a good question. These specs were pulled from aftermarket literature. I'm assuming these specs reflect use of a starter caps; however, I can't be certain.
  • Do they use a hard start cap? That significantly reduced the initial amperage load on my Coleman MachIII.