he said he removed the fixtures
IF the fixtures are removed, the string should be disconnected
depending on where the "wire Nuts" or splices are tied together
break the parallel connections at the first fixture
work his way back or forward from there
find the section where the fuse blows, or doesn't
you find the section that has the screw thru the wiring
it will be a roof screw, around the vents, fans, A/c etc..
very unlikely to be and edge screw for the moulding/trim unless it is right above the fuse panel location, in their path from wall to ceiling, put that is a possibly
IF the fixtures are removed, the string should be disconnected
depending on where the "wire Nuts" or splices are tied together
break the parallel connections at the first fixture
work his way back or forward from there
find the section where the fuse blows, or doesn't
you find the section that has the screw thru the wiring
it will be a roof screw, around the vents, fans, A/c etc..
very unlikely to be and edge screw for the moulding/trim unless it is right above the fuse panel location, in their path from wall to ceiling, put that is a possibly