whs9841 wrote:
Chris, a few questions about your response:
1. If I piggyback the SPP6 on the larger capacitor, do I just connect the wires from the SPP6 to the two different posts on the larger capacitor?
Yes- exactly.
2. Is there a way to wire the SPP6 as a compressor start capacitor for this a/c?
That's what it will be doing- added to the compressor run capacitor.
3. How would the SPP6E benefit me more in this scenario? How would it be hooked up to the A/C with the existing capacitors?
The difference between the E sries and standard series is that the E series uses a speed sensing relay to take the start capacitor out of the circuit, the standard uses a PTCR, which simply gets hot and stops conducting, taking the capacitor out of the circuit. For normal use this works well, and is cheap. However, when running on a generator, the generator will usually bog down for a second, and because the PTCR is basically time based, it takes the start capacitor out of the circuit before the compressor is running at speed. The E series keeps it in the circuit until the compressor is running at ~75% speed.
Supco doesn't recommend the E series because if you cycle the compressor off and right back on, the capacitor is in the circuit for too long a time, because the compressor cannot start against the high pressure. This is harder on the compressor.
If you don't run on a generator, the E gives no advantage, but it can make the difference between starting and not when running on a marginal genset.
You want a single start kit- more is not better.
FWIW, there are actually better kits out there, though they are a bit more complicated to install. They use 3 wires and a true potential relay. Dometic makes a factory start kit specifically for the Penguin and Onan 2.8.