Forum Discussion
31 Replies
Sort By
- Now look at the graph at the 200% level. Close to a minute to open. That is 400 amps close to a minute before that 200 amp class T opens. Your call.
Search for ANL and you will see much faster open at 200%. - Bigfoot2005Explorer
time2roll wrote:
200 class T is fine. I would use 150 amp. That is all I am saying.
GP also say #2 wire and 2/0 is getting installed.
https://www.bluesea.com/products/5112/Fuse_A3T___Class_T_110_Amp
Ampacity of #2 with 105C insulation is 210 amps
Ampacity of 2/0 with 105C is 330 amps
http://www.genuinedealz.com/voltage-drop-calculator
They suggested 2/0 wire to me if I am going to do a longer run of wire as I might have too to avoid a voltage drop - 200 class T is fine. I would use 150 amp. That is all I am saying.
GP also say #2 wire and 2/0 is getting installed.
https://www.bluesea.com/products/5112/Fuse_A3T___Class_T_110_Amp
Ampacity of #2 with 105C insulation is 210 amps
Ampacity of 2/0 with 105C is 330 amps
http://www.genuinedealz.com/voltage-drop-calculator - Bigfoot2005Explorer
time2roll wrote:
Class-T will pass 2x rating for 60 seconds. That 1500 would have to draw 300 amps for a full minute to open. Not going to happen during normal operation. Check Blue-Sea graph.
Not sure what you are saying. The manufacturer recommends the Class T fuse rating of 200 amps for their 1500 watt inverter.
1100 – 1800W inverters 200 amp #2 AWG - Class-T will pass 2x rating for 60 seconds. That 1500 would have to draw 300 amps for a full minute to open. Not going to happen during normal operation. Check Blue-Sea graph.
- MEXICOWANDERERExplorerThen so be it. They are the Supreme Court. Cheap inverters have little or no reserve punch and the manufacturer knows their product. :)
- Bigfoot2005Explorer
MEXICOWANDERER wrote:
Too tight of protection may blow a fuse. How? Inverters are rated for overcurrent to start a load that draws a lot more than nameplate design. My recommendation if to check with the manufacturer or vendor.
My Trace is rated to start stuff to nameplate rating times eight.
Manufacturer recommends 200 amp T fuse for the 1500 watt inverter - MEXICOWANDERERExplorerToo tight of protection may blow a fuse. How? Inverters are rated for overcurrent to start a load that draws a lot more than nameplate design. My recommendation if to check with the manufacturer or vendor.
My Trace is rated to start stuff to nameplate rating times eight. - 200 amp ANL is fine. I would go a little tighter with Class-T with 150 amps.
- ktmrfsExplorer II
GordonThree wrote:
Spend a bit more and get a class T fuse and holder. Look at the short circuit current of your battery bank and the interrupt capability of the fuse.
x2. and mount it as close to the battery as possible.