look at page 25 of the manual. The 10/15 units require 200 amp fuse, the 20/25 require a 300 amp fuse.
Needless to say that wire must be increased accordingly.
Yes, you could leave the 200 amp fuse and wire, but will not have the full benefit of the freedom 20.
Needless to say that wire must be increased accordingly.
Yes, you could leave the 200 amp fuse and wire, but will not have the full benefit of the freedom 20.