rlsem's avatar
rlsem
IOTA ITS-50R Transfer Switch Failure
Just experienced a IOTA ITS-50R Transfer Switch "melt down". Fortuneately we were in the RV when the incident occurred. Total loss of shore power. Battery source OK. Fridge OK. MicroWave oven did not survive, One TV smoked. Ground Fault circuit breaker will not reset.
Service Technician arrived and located the problem. Melted IOTA ITS-50R Transfer Switch. No replacement available at time.
Remedy: tech removed switch and wired around to get us operational. (Wire Nuts and Tape) Replaced the GF breaker.
Question:
the RV is wired for a generator, however, We do not have a generator on board. Am I okay to leave the Transfer Switch out? Maybe improve the wiring situation by putting it in a junction box? Or, if I must replace the switch, which is recommended.
2010 Cameo by Carriage
37ft 5th Wheel
Please advise...
Rick Smith
rlsem
  • If NO Genset, there is no reason to install a ATS. Hardwired with rated wire nuts is OK. I hope he also wire nutted and taped off the 3 feeds from the Genset compartment. If someone added a genset in the future, those wires will be hot when the genset is started. I would put a note on the Geset area wiring 120 box that the ATS has been removed for any future owner or repair Tech. Doug