Possible a tripped GCFI outlet upstream of those dead outlets
Possible loose wires on outlet upstream of those dead outlets
Possible tripped inverter
But this statement is confusing
" however no voltage to two breaker coming of the bar the breaker connect to."
Do you mean that 2 circuit breakers in AC Panel have no voltage going to them?
IF you have no voltage measured at load side terminal (where wire connects) with breaker CLOSED----then breaker has failed OR is tripping free (not resetting) due to short downstream
Would need to remove wires.....pull breaker and check if lugs are broken and try another breaker.