obscenic's avatar
obscenic
Low propane at furnace
With a U-tube manometer I have measured 11" WC at the propane regulator output. When I fire up the furnace the WC drops to just about 10.5". When I measure at the furnace, at the post-valve gauge output, I see just 6" WC when the furnace fires. Any idea what could be causing this?
  • I read in the Dometic manual that you need 50% of the gas appliances operating then set the regulator to 11"WC. When I did my testing I had 8" at the Refrigerator test port and the reefer would not cool on gas so I replaced the regulator with 1 that I could adjust at the tanks I got it set to 11"WC with all 3 burners on the stove top on max and the reefer on, now the reefer cools to 34 degrees.
  • Static w/c should be 11.5. You should NOT see a drop below 11 inches when an appliance is running. 6 inches at the furnace is strange. Regardless, IF you have to adjust a LP regulator that has been in use for years, it is BEST to replace the LP regulator. This is because a Regulator can get a weak spring/diaphragm and you can never get the W/C to stay on target as it will hunt and surge up and down. Doug