pianotuna wrote:
Hi Mex,
Also "load support" is NOT voltage support.
There is no information about duty cycle, and of course, there probably is one.MEXICOWANDERER wrote:
Even load SUPPORT is misleading. The function of inverter paralleling is to assist a generator in the STARTUP of a load.
Such points as DUTY CYCLE must be applied toward the inverter. X time for X watts of paralleling support. Boosting startup is supposed to take place in seconds, not minutes or hours, regardless of the size of the battery bank. Check with OEM if you question this.
I cannot find anything in the manual. Not sure why there would be. In load support the inverter section is just acting like an inverter. As long as you do not exceed the continuous rated output of the inverter section, then it should be fine provided adequate air flow for cooling and such.
Are people understanding that this inverter passes through AC current? Up to 60 Amps! All the inverter has to do is invert from the batts and sync to the passing through AC signal.