Forum Discussion
hbski
Sep 08, 2016Explorer
MEXICOWANDERER wrote:
.....Check with OEM if you question this.
I don't, but went ahead and checked for everyone else's benefit:
--------------------------
ME:
regarding MSH3012M
A Question came up regarding load support. Is there any limit on the duration of a load support cycle with the magnum? That is beyond the other system parameters?
As an example, If I were to use a generator capable of 15 Amps AC to run a continuous load of 25 Amps AC with the load support of the Magnum supplying the remaining 10 Amps AC?, is there any reason to think that I could not do this indefinitely until I've fully depleted the useful capacity of my battery bank?
-------------------------
Magnum tech reply:
Good Afternoon,
Will load share until you reach LBCO. ( low battery cut out )
-------------------------
any other questions?