Also from the manual:
The full AC continuous pass-thru capacity of the MSH-M Series inverter/charger is limited to
60 amps. The AC input to the inverter requires a 60-amp continuous duty rated breaker, which
corresponds to a minimum cable size of #6 AWG or 13.3 mm2. If you are using other circuit
breakers/wire sizes, refer to the appropriate electrical codes for sizing requirements.
The full AC continuous pass-thru capacity of the MSH-M Series inverter/charger is limited to
60 amps. The AC input to the inverter requires a 60-amp continuous duty rated breaker, which
corresponds to a minimum cable size of #6 AWG or 13.3 mm2. If you are using other circuit
breakers/wire sizes, refer to the appropriate electrical codes for sizing requirements.