Forum Discussion
landyacht318
Apr 01, 2018Explorer
Amazing how in the quest for automatic, function is compromised to the degree it is.
Unless the magnum has its own amperage measuring device, seeing what the battery is accepting, then end amps can never be programmed correctly as any loads on the battery will throw it off.
My manual adjustable voltage charger becomes more and more simple. Watch ammeter, twist dial accordingly.
I also do not see any possible use for a charger, which is completely guessing as to state of charge, allowing the option to stop charging at anythig other than what it tinks is 1005 state of charge.
gee, no, 92% is just fine, stop charging there.
I don't know how you are going to achieve it, but if you want these batteries to get fully charged, hold absorption voltage until amps INTO the 800 AH of batteries, tapers to 4.
Unless the magnum has its own amperage measuring device, seeing what the battery is accepting, then end amps can never be programmed correctly as any loads on the battery will throw it off.
My manual adjustable voltage charger becomes more and more simple. Watch ammeter, twist dial accordingly.
I also do not see any possible use for a charger, which is completely guessing as to state of charge, allowing the option to stop charging at anythig other than what it tinks is 1005 state of charge.
gee, no, 92% is just fine, stop charging there.
I don't know how you are going to achieve it, but if you want these batteries to get fully charged, hold absorption voltage until amps INTO the 800 AH of batteries, tapers to 4.