Aug 24, 2023Explorer
Micro Air Easy Start 364-XP installation
I installed a Micro Air Easy Start 364-XP on our Furrion AC unit and it has been generating issues from the start, making me wonder if I had installed it incorrectly or something else.
For starters, I was trying to run/test the unit on our 15amp outlet. Turns out the Furrion draws 15.35amps when running, so of course on the small breaker and smaller extension cord the compressor would fire up, run for a minute or so, and then shut down/stall out. Makes perfect sense.
Next test was to get a 25’ 30amp RV extension cord. Plugged it into a 20amp outlet. Fired it up, the compressor ran for about two minutes (I was getting excited) and then shut down. The fan ran for three minutes, the compressor kicked in, ran for 30 seconds and shut down again. This time the error lights signifies an over current situation, saying the device was not able to support the load. Not sure I buy that.
Any thoughts? I’ve been working directly with Micro Air Support, but curious if anyone has had any issues with installing this unit on a Furrion 15k btu AC unit? I’m pretty sure the way it’s running that everything is wired correctly, but just have that sneaking suspicion something’s not right? I don’t know where to go with this. And it’s 100° here in WI. Of course.
For starters, I was trying to run/test the unit on our 15amp outlet. Turns out the Furrion draws 15.35amps when running, so of course on the small breaker and smaller extension cord the compressor would fire up, run for a minute or so, and then shut down/stall out. Makes perfect sense.
Next test was to get a 25’ 30amp RV extension cord. Plugged it into a 20amp outlet. Fired it up, the compressor ran for about two minutes (I was getting excited) and then shut down. The fan ran for three minutes, the compressor kicked in, ran for 30 seconds and shut down again. This time the error lights signifies an over current situation, saying the device was not able to support the load. Not sure I buy that.
Any thoughts? I’ve been working directly with Micro Air Support, but curious if anyone has had any issues with installing this unit on a Furrion 15k btu AC unit? I’m pretty sure the way it’s running that everything is wired correctly, but just have that sneaking suspicion something’s not right? I don’t know where to go with this. And it’s 100° here in WI. Of course.