Onan Microlite KV - model 2.8KVFA26100K - spec K Generator was starting and running 120 no load 115 load for 20 minutes and would die. Gradually reduced running time to under 2 minutes. ...
When was the oil changed? I bought a WW once and the 2800 would die when I loaded it. Changed the oil and wala. The oil I drained out was as thin as water. It never gave me a problem after that. The PO just neglected it. Shame it was neglected that way.