So, here goes:
Bank... 430Ah, four 6's, ocv @ 12.44v, 74%soc, -111Ah's
Solar... two 140w 12v poly panels, in series, manually tracked, thru 50' of 6awg to a Tracer 3215BN MPPT charge controller and MT50 Remote Monitor.
10:50am:
- clear skies
- Isc at the moment was 'about' 9a (x2). (clamp meter not that reliable)
- Voc 20.6v
10:55am:
at Panels... 7.9a @ 31.2v,
at Bank... 18.9a @ 13.0v
The highest amperage I saw all day was at 11:05am, with 19a to the bank. Mostly in the mid 17's to high 18's up until about 3pm. I was a little surprised, given the conditions. A couple days earlier, under mostly cloudy skies, I saw amps in the high 21's several times... but that may have been an edge of cloud effect thing?
At 1:15pm, I switched over to the Solar30 pwm, and saw a difference of 1a to the bank, 17.3a vs 18.3a, for a 5.5% increase by the mppt controller.
Back on mppt, throughout the afternoon amps tapered to the mid 13's range by 6:40pm, and by 7:40pm, amps to bank were in the high 7's.
(At 5:15, I laid the panels flat, east to west, and saw a difference of 5.4a to the bank, 10.4a vs. 15.8a, for a decrease of 35%, compared to tracked.)
Thanxx!
My "standard" for expected max amps to the 13v battery for aimed panel wattage is based on 130w-8.2a, so 280w should yield 280/130 x 8.2 = 17.66 amps
You got 19a with MPPT and 17.3 with PWM (at different times), so IMO your set-up is working just fine! :)
Choosing the Tracer, with its high Voc limit to let you put 12s in series, was obviously the right choice over the Eco-W with its limitation of 42 or 45 Voc that means it can only do one 24v panel but not two 12s.
I don't fuss about getting to 100% every day on solar. Sometimes you do and often you don't. As long as you get to 100% once in a while and do shallow cycles like 75-95s, you don't need to EQ much if ever. The SG will tell you how that is going.
Good report!