time2roll
Jan 30, 2015Nomad
BFL13 wrote:pianotuna wrote:
53 watt panel
PT, those guys are as bad at math as your are! :) The USA NEC says you need a 20% margin but these guys say you should multiply by 1.25 for controller size in amps. That is a 25% margin.
Hint for the "math disadvantaged"--
- 25 expected amps. 20% is 5 amps so you need a 30 amp controller.
1.25 x 25 = 31.25 (6.25 more not the NEC required 5 more.)
NEC says 20% margin on the wire/equip for continuous duty (3+ hours).
30 amp x 20 % = 6 amp derate or 24 amps. Or as they suggest 1.25% of the 24 amps.... wait for it..... 30 amps.
So the 1.25 is same as NEC 20% because they are going in opposite directions.