KD4UPL wrote:
BFL13, what is the NEC reference about a "20% margin". That's pretty vague.
.
OK I may have been wrong on that. I will try to find where I picked up that 20% margin for NEC idea.
This says that the actual NEC rule is for a 25% margin, by multiplying by 1.25.
It says NEC does not apply to autos, trains, etc. Not clear about RVs.
From:
http://www.senecass.com/NEC2000.pdf"The ampacity of conductors in PV source circuits shall be at least 125% of the rated module or
parallel-connected modules short-circuit current [690-8]. The ampacity of the PV-output circuit
conductors shall be at least 125% of the short-circuit output current [690-8a]. The ampacity of
conductors to and from an inverter or power conditioning system shall be 125% of the rated
operating current for that device [690-8a]. In a similar manner, other conductors in the system
should have an ampacity of 125% of the rated operating current to allow for long duration
operation at full power [215-2]. These NEC requirements are to ensure that the connected
overcurrent devices or panelboards operate at no more than 80% of their ampacity. Operation
when snow or cloud enhancement increases the PV output above normal may require additional
ampacity. Daily expected values of solar irradiance will exceed the standard test condition of
1000W/m2 at many locations."