the t stat only operates one unit, the main one i am working on
well, that worked great! put on the supco spp6 from the other unit and it started right up. was pulling about 14 amps as it was running. the fan pulls about 3 amps so the compressor was pulling 11, and the compressor RLA is 10.7 so that should be good, right? it didn't seem to be as cold of air as i would have liked though.
any thoughts on what i should do with the Dometic A/C WSX-5 Motor Starter that is on the old start capacitor? should i keep it on there?
well, that worked great! put on the supco spp6 from the other unit and it started right up. was pulling about 14 amps as it was running. the fan pulls about 3 amps so the compressor was pulling 11, and the compressor RLA is 10.7 so that should be good, right? it didn't seem to be as cold of air as i would have liked though.
any thoughts on what i should do with the Dometic A/C WSX-5 Motor Starter that is on the old start capacitor? should i keep it on there?