Chakara's avatar
Chakara
New EMS shows Open Ground ?
Hey guys - was hoping some of you could check my sanity.  Here at the house I have a 30A RV hookup next to the trailer.  I plug the trailer in via an 30/50 amp adapter.
I  just completed the install of the EMS-HW50C 50 amp hard wired system.  I plug in the rig and low and behold, the EMS show EC#2 - Open Ground.
Yikes!  How long have I had that problem?
I did a bit of reading and busted out the old Fluke.  Here is what I get
Pedestal no load:
Hot to Ground:       123V
Hot to Neutral:        123V
Neutral to Ground:  0V
Input to EMS - no load:
L1 to Ground:         123V
L2 to Ground:         123V
L1 to Neutral:          123V
L2 to Neutral:          123V
I'm not an electrician, but this all seems normal.  This is where I got a little brave (foolish?? :) ) and flipped the bypass switch on the EMS.  Trailer lights up and everything works.  I put a little heater as a load and the only different measurement with a load on is:
Neutral to Ground:    1.3V
Again, I think that when you have a load you should read some voltage on that link so it still feels normal?
Before I call Progressive Ind. for an RMA - - can anyone who knows more about electricity confirm my finding?  Or am I stupid and my trailer is going to burst into flames :)
Thanks all!
-Kyle
  • Since you verified the problem isn't real by getting 120V to ground, I would double check the wire connections inside the EMS.
Having RV issues? Connect with others who have been in your shoes.24,343 PostsLatest Activity: Dec 17, 2025
