he has a spare charger/converter
yes ground to the frame with the Ground lug
but run a NEG wire all the way to the batteries
do not use the frame for the negative path
do not ground the inverter to the NEg cable/the batteries
the negative power path and the safety ground/frame path
are two separate physical and electrical paths
never mine that they will read continuity with a meter
they are individual physical circuits
connecting the inverter ground to the NEg cable/battery can induce AC into the DC path
it also removes the safety factor.. the safety factor to be real the ground is frame ground, not battery negative