Aug 30, 2016Moderator
Almot
according to Mexi's previous posts
charge at 14.4 until charge rate drops below 1% of ampHr capacity
aka 500ampHr bank charge at 14.4 until amps in are 5amps or less
then turn off charger until next charge cycle
If possible charging current of a bank with an SOC of 70% or less
should be c/5 aka 20% of capacity, in this example try for a starting rate of 100amps end at 5amps
this negates the need of the 'equalization conditioning charge'
my PD70 will only do about 12% of my 675 ampHr bank
but since i need the genny for the A/C i am charging until full
this winter, the charging profile will change some, but so will my overnight use
according to Mexi's previous posts
charge at 14.4 until charge rate drops below 1% of ampHr capacity
aka 500ampHr bank charge at 14.4 until amps in are 5amps or less
then turn off charger until next charge cycle
If possible charging current of a bank with an SOC of 70% or less
should be c/5 aka 20% of capacity, in this example try for a starting rate of 100amps end at 5amps
this negates the need of the 'equalization conditioning charge'
my PD70 will only do about 12% of my 675 ampHr bank
but since i need the genny for the A/C i am charging until full
this winter, the charging profile will change some, but so will my overnight use