drillagent wrote:
Thank you all for your input. I decided to check the coil on the back of the fridge and the tank is hot, but the coil above is cold to the touch. Is this a bubble, or normal? I'll try to wedge a fan in there to blow upwards and see what happens. Where is the thermal switch for the fans? The fridge is not in a slide and the vent is located on the roof. Thanks again for all your help.
You have to pull the refer to access both the 2 fans and the Thermostatic switch The switch is on the condensor fins at the back top of the refer. When I repair the fans or tstat, I ALWAYS replace both Fans and the Tstat for the fans. Because you have to pull the refer. I also run a 2 wire pigtail from the Tstat down the back of the refer and secure it by the control board. That way you can jump the wires to test fan operation in the future if the tstat fails again. If the tstat does fail again you just connect both wires and the fans will then run. Doug