Searched the forum and was surprised I didn't find anything on this topic. We are taking our TT on our first boondocking adventure next week and wanted to test out our new Champion inverter/ generator. Got it running, plugged in TT and my PI (hard wired) EMS tripped with an open ground error. In the past I've hooked up my TT to my old generator without grounding it and the EMS didn't detect and issues but it's also a big metal frame unit with metal legs on the ground. Before I go buy grounding rod I was just wondering if other people with inverter/generators normally ground them, like manual says you should ;). Thanks!
  • time2roll wrote:
    Or just use the bypass.
    Bypass does not remove the EMS entirely from the circuit, just the EMS section, surge protection circuit is still in play. G-N bond is the solution.
  • Or just use the bypass. If generator voltage is an issue it will shut down from overload before any issues to the RV happen.
  • rjxj wrote:
    Normal for most generators to be open ground.
    The OP's Champ inverter genset doesn't have an "open ground" but rather a floating neutral that his PI EMS interprets as an open ground. Simply adding a G-N bond is safe and will solve this issue.
  • Easily made for $2 or $3, you don't need to buy the expensive one from Progressive Industries.
    Go to any big box hardware store and buy a 3 prong plug. Take a short piece of wire, 1" to 2" long, and strip both ends. Put those stripped ends under the screws for the NEUTRAL prong and the GROUND prong. DO NOT PUT ANYTHING ON THE HOT PRONG!. You are done. This does have to be plugged into the generator. Putting it somewhere in the RV won't work. (Of course, put the cover back over the wire. This picture left the cover off for clarity.)
  • Normal for most generators to be open ground. The ground is always bonded at the source such as at the panel for your house or the campground pedestal. You can make a bonded plug to use on your generator.