enblethen wrote:
Turning off breakers or on will not show a GFCI issue as breakers do not open ground or neutral leads. You must physically open that portion of the system. Problem could be any where in the 120 volt AC system.
Refer, water heater equipped with 120 volt AC element or converter would be places to start.
wrong, wrong wrong. opening a breaker will tell you if a given circuit has a ground fault, if the hot lead is open, which it is when the breaker is tripped, then there is no current flowing and no way to trip the GFI for a current imbalance in that circuit. close the breaker and if it trips the GFI then there is a ground fault in that circuit. So, it's a way to find which circuit has an imbalance.
If the GFI trips with an open breaker downstream, then the GFI is telling you there is a ground neutral bond in the ciruit.
so in the case of the OP, breakers are a good way to isolate the problem within a circuit.