Salvo wrote:
A couple of test questions.
1. Why 60Vac?
2. Why does the analog voltmeter read about 6V (from gnd to neutral or gnd to hot)?
Salve7prt wrote:
1) The hot and neutral wires will each carry about 60VAC. You will see 120VAC hot to neutral and hot to ground, though.
Cheers!
Mike
I recall answering both of those recently though the 2nd one by inference.
A1: Due to capacitive coupling between the wires forming a voltage divider.
A2: Due the the lower impedance of the analog meter "loading" the divider (Which can only handle a very small amount of current)