You have two surge devices.......one at pedestal and another hardwired.
Both show good voltage and no open neutral yet the NEW TV and Vac burnt up again?
Then you still have an open neutral....either in transfer switch or main AC panel.
Did this top notch dealer even check the wiring connections inside your rig?
Until you find and correct the open neutral you will continue to burn up TV, Vac and microwave.........bet they are all feed from same bus bar in AC panel.
50A--110V and open neutral will cause 220V on one leg of 50A service.
Once again I suggest you contact MFG. directly and get a factory rep involved. There is a serious issue with the wiring and it is a factory problem.
Both show good voltage and no open neutral yet the NEW TV and Vac burnt up again?
Then you still have an open neutral....either in transfer switch or main AC panel.
Did this top notch dealer even check the wiring connections inside your rig?
Until you find and correct the open neutral you will continue to burn up TV, Vac and microwave.........bet they are all feed from same bus bar in AC panel.
50A--110V and open neutral will cause 220V on one leg of 50A service.
Once again I suggest you contact MFG. directly and get a factory rep involved. There is a serious issue with the wiring and it is a factory problem.