Space heater is not considered a continuous load device as it will cycle some(generally). Same as a hair dryer can go to 1875 due to short use. Actually I believe both of these ratings (1500 & 1875) are at 125 volts giving the max allowed by NEC at 12 amps (continuous) and 15 amps (short use)
Converter is a continuous rated (120 volt) device so the circuit is derated to 80% or 12 amp max on 15a circuit. Needs 20 amp circuit with 16 amp continuous rating. Amp load will actually increase to an extent with low voltage. Space heater the amps drop as voltage drops.
NEC defines continuous as 3 hours at max rating.
Converter is a continuous rated (120 volt) device so the circuit is derated to 80% or 12 amp max on 15a circuit. Needs 20 amp circuit with 16 amp continuous rating. Amp load will actually increase to an extent with low voltage. Space heater the amps drop as voltage drops.
NEC defines continuous as 3 hours at max rating.