- wnjjExplorer IISounds to me like the neutral on the 20A generator receptacle isn’t the same as the neutral on the 30A. One of them must be hot-neutral swapped. Is there continuity between neutral on the 20A and 30A (generator off)?
- 185EZExplorer
road-runner wrote:
185EZ wrote:
I don't have an EMS, but I think there's a very good possibility the EMS will diagnose the dogbone provided power as defective. Somebody with a 50 amp EMS can say this with more certainty. You said the EMS is happy with house current. Is this from a 240 volt outlet? If so, plug into 120 volt shore power using the dogbone and see what the EMS says.
Sorry, didn't think the 50 amp would make a difference with the generator thing.
only one dogbone 30 amp male to 50 amp female
I have a EMS PT50X
I have 120v 30 amp service at home and the dogbone works fine with the 50 amp EMS.
I have also plugged into a campground 50 amp and EMS works fine.
I let the generator and EMS do it's thing before I plug it into the rv.
Doesn't really make a difference since the EMS won't let power through at this time whether the cord is plugged in or not.
I think the EMS is doing a great job but maybe too good.
Like going to the doctor.
Hey Doc I feel great
Well our tests prove otherwise.:(
Everything was good until the bonding plug
I'll just deal with no EMS and an open ground. Pretend it never happened, lol. - road-runnerExplorer III
I have a EMS PT50X - road-runnerExplorer IIIBeing a generator that none of the rest of have likely used, there could be something "different" about it. For example, maybe the outlets are miswired, with hot and neutral swapped between the two duplex receptacles. Another possibility, maybe the generator's waveform is sufficiently flawed to be triggering some error in the EMS. Maybe there's a wiring fault in the RV that's not showing up with shore power or the internal generator. One thing that's different with this generator is that the DC output doesn't have its own winding, but rather uses a tap on the main winding. But overall, I don't see anything in the Gen4000DF wiring diagram that looks like an issue. The wiring diagram is on page 30 of the manual at this link: http://www.buffalotools.com/manuals/gen4000df-ssmanual2017_sf.pdf
- 185EZExplorerSorry, didn't think the 50 amp would make a difference with the generator thing.
I have a EMS PT50X - Now we have a fifty amp rig. Lots of items that can be effecting readings. 120 volt AC water heater elemnet for one.
What combination of adapters are you using to plug rig into the genset? They are a problem in many cases! - 185EZExplorerquick recap
50 amp cord works fine with EMS and house current
onboard 7000kw genset works fine
1st portable generator would have hz vary ALOT, 58 to 98hz, and EMS wouldn't let power through.
Funny thing is when it did let power through there was no open ground fault.
If plugged into rv without EMS it would give a fault code to charger/inverter but power up other appliances and a/c.
Got a 2nd portable generator. 60 to 61hz.
But showed an open ground and wouldn't let power through
Disconnected EMS and all good with the rv
I think I'll leave EMS out before I screw something up - You need to back up a little!
First you may read continuity as some devices in the rig will cause this.
Open the 120 volt power distribution panel. Turn off all circuit breakers. Check between the white(neutral) and the green or bare ground wire. You should have continuity from genset cord body with jumper.
Check between the black and the ground. You should not have continuity.
If you do not have as shown, then unplug the rig's shore power cord. verify the cable to insure it is wired correctly. Has some one replaced the rig's cord body? Check it. - 185EZExplorerEMS removed
RV
Generator not running plugged into rv
Bonding plug in
No continuity between neutral and ground in any receptacle in rv.
Only continuity between neutral and hot
Generator
Bonding plug in
Continuity between ground, neutral and hot
Bonding plug out
continuity only between neutral and hot, same as rv - wnjjExplorer IIWhat Drew said.
To further test, turn the generator OFF but leave the RV and the bonding plug connected. If you then go inside the RV, there should be continuity between the ground and neutral of any receptacle. That is what the EMS is looking for. If, for example, your RV shore power cord has them reversed you’ll instead find that hot and ground are shorted.