shinybeast
Apr 10, 2014Explorer
Thanks for the replies. BFL13, the cooperbussman link was just what I was looking for. If I have it right for my stuff...
(3-1)*7.5=23.4
I'm using #10 wire (30A max) which is over the 23.4A calculated above so I don't need fuses at panels, correct?
I read somewhere that if one panel in a string of three or more in parallel failed somehow, the current from the others could/would start a fire as it overloaded the bad one. Being new to solar I felt compelled to seek out the safest way to setup and use my new gear with my new TT.
(3-1)*7.5=23.4
I'm using #10 wire (30A max) which is over the 23.4A calculated above so I don't need fuses at panels, correct?
I read somewhere that if one panel in a string of three or more in parallel failed somehow, the current from the others could/would start a fire as it overloaded the bad one. Being new to solar I felt compelled to seek out the safest way to setup and use my new gear with my new TT.